Hi,
Calculating a 20A 277V pole lighting circuit along the driveway of a large industrial site.
16 fixtures, total of 1,975 foot run. Calculation (see below) gives 6.91% voltage drop at the farthest fixture. Typically, I'd consider this too much, however the fixtures are modern "Universal Voltage" and accept 120-277V. The far fixture would be getting 257V and would be perfectly happy. Aside from violating the "recommendation" in the NEC regarding voltage drop, I don't see a problem. At these distances, upsizing the wire more does not give significant improvement, unless I go to silly sizes ($$$). I'm already at #8 to the first fixture and #10 from there.
The only other real issue I can see would be the effect on clearing time of the breaker, but I don't really know how to quantify that. The total current is only 6.75A, so I could drop the breaker to 15A for faster tripping.
A similar scenario is playing out with the indoor circuits for the 180 high output highbay fixtures.
Thoughts?
P.S., the spreadsheet is an iterative calculation, so it takes into account the increased amperage due to decreasing voltage along the circuit.

Calculating a 20A 277V pole lighting circuit along the driveway of a large industrial site.
16 fixtures, total of 1,975 foot run. Calculation (see below) gives 6.91% voltage drop at the farthest fixture. Typically, I'd consider this too much, however the fixtures are modern "Universal Voltage" and accept 120-277V. The far fixture would be getting 257V and would be perfectly happy. Aside from violating the "recommendation" in the NEC regarding voltage drop, I don't see a problem. At these distances, upsizing the wire more does not give significant improvement, unless I go to silly sizes ($$$). I'm already at #8 to the first fixture and #10 from there.
The only other real issue I can see would be the effect on clearing time of the breaker, but I don't really know how to quantify that. The total current is only 6.75A, so I could drop the breaker to 15A for faster tripping.
A similar scenario is playing out with the indoor circuits for the 180 high output highbay fixtures.
Thoughts?
P.S., the spreadsheet is an iterative calculation, so it takes into account the increased amperage due to decreasing voltage along the circuit.