I am feeding roadway light poles about 200 feet on center with 277 volt and using a common neutral. The first pole will be on phase A, the second pole on phase B, the third pole on phase C, the fourth pole on phase A. the fifth pole on phase B and so on. Since I am using a common neutral I think Current Flow gets involved and Vector Analysis gets involved. Is there a computer program that I can use and if not is there a long hand formula that I can use. Some of the circuits are long (1500 to 1800) feet from the panel source. I need to make sure I am not exceeding a total of 5% VD.--If I use the conventional VD formula I think the answer will be larger than it really is with using a common neutral. I need to minimize my wire size so I am trying to find the correct computer program or long hand formula.-- I would appreciate any help I can get. Thanks. My e-mail address is --