Generally no.Originally posted by redfish:
Does it matter which end of the circuit you install the larger wire to compensate for voltage drop?
Value engineering.Originally posted by rattus:
Why would you use different sizes in the same circuit?
I think to classify this as a "simple circuit" you would need only one load. How about you calculate it again with one load and a JB in the middle instead of a load dropping off.Originally posted by iwire:
I am 2.5 volts better off with the larger wire at the front of this simple circuit.
It's my circuit and I will wire it how I want.Originally posted by hardworkingstiff:
Which one?Originally posted by physis:
Bob you should calculate your 6 AWG for only 10 amps. to make your voltage drop 1.96 v. instead of 3.9.
No doubt.Originally posted by rattus:
Generally speaking you would use the larger wire where the current is greatest, but depending on the relative wire lengths, this might not always be the best solution. Each case would have to be computed individually.