Have 3 airport hangers. 1675 feet from main road, to the Existing Overhead poles.
Would it be ok to run Underground 750mcm
Would require 2 manhole I guess @ 550, and 1100 feet. 120/208volts. 3 phase. Hangers don't use much.
They asking for about 3 - 20 amps circuits per bay ( 12 bays per building, 3 buildings) 300 long by 50 wide, 20 feet high.
1ckt for 2 - 150 watt HID lights
1ckt for 1hp Bifold door.
1 ckt for GFI general use
Each building would get 7- 400 watt MH wallpacks.
Plan on feeding the 3 buildings. ( 1 - 150 amp MB panel 1 phase) per building.
Service from street. Will be 3 phase 400 amps. But the Load calc will definitely can diversify, Due to only a fraction of use in the hangers. What diversify % I would have to estimate.
From the 400 amp Service to Each 150 amp 1phase MB panel - Run 2/0 about 200 feet each
Then from 150 amp 1 phase panels to the (12) Small subpanels per blg. Fused @ 40 longest being 300 ft to last bay.
Was calculatings voltage drop from street to farthese panel.
(1675FT) -From over head poles to Main Blg service ( #750 MCM) 400 amp-3phase -120/208 #2/0 -150 1 phase panel( 200 FT) , + 150 mb panel 1 phase to farthest Panel #6 (300ft)
Would it be ok to run Underground 750mcm
Would require 2 manhole I guess @ 550, and 1100 feet. 120/208volts. 3 phase. Hangers don't use much.
They asking for about 3 - 20 amps circuits per bay ( 12 bays per building, 3 buildings) 300 long by 50 wide, 20 feet high.
1ckt for 2 - 150 watt HID lights
1ckt for 1hp Bifold door.
1 ckt for GFI general use
Each building would get 7- 400 watt MH wallpacks.
Plan on feeding the 3 buildings. ( 1 - 150 amp MB panel 1 phase) per building.
Service from street. Will be 3 phase 400 amps. But the Load calc will definitely can diversify, Due to only a fraction of use in the hangers. What diversify % I would have to estimate.
From the 400 amp Service to Each 150 amp 1phase MB panel - Run 2/0 about 200 feet each
Then from 150 amp 1 phase panels to the (12) Small subpanels per blg. Fused @ 40 longest being 300 ft to last bay.
Was calculatings voltage drop from street to farthese panel.
(1675FT) -From over head poles to Main Blg service ( #750 MCM) 400 amp-3phase -120/208 #2/0 -150 1 phase panel( 200 FT) , + 150 mb panel 1 phase to farthest Panel #6 (300ft)