A property owner wants to run power to 3 new lighting fixtures that is over 300 feet from the nearest panel. He wants to use #14 AWG on a 15 amp circuit. How does this affect wire and breaker sizing.
It affects wire size, as Dennis has already mentioned. It does not affect breaker size. You could improve the voltage drop situation by using #12 wire, and still keeping the 15 amp breaker. But you would have to use #12 for the equipment grounding conductor, as well as for the hot and neutral wires. But it all comes down to total load. What size of lights (i.e., in terms of watts) is the owner planning to use? Are LED lights being considered?How does this affect wire and breaker sizing.
Voltage drop is dependent on the load. What is the wattage of the fixtures? IMO the owner is out of his mind and depending on the fixtures this may not be enough to run the fixtures effectively
He will be using motion sensors, he considers them for security. Two 100 watts at each of 3 locations.
On the bright side (no pun intended), if it's an incandescent fixture, he will have good bulb life
Depends on voltage too. If it were 277 volt lighting you can drop more volts then you can @ 120 volts and still be within a certain percentage.
He will be using motion sensors, he considers them for security. Two 100 watts at each of 3 locations.
A property owner wants to run power to 3 new lighting fixtures that is over 300 feet from the nearest panel. He wants to use #14 AWG on a 15 amp circuit. How does this affect wire and breaker sizing.
With just 5 amp load there would be a 6 volt drop at 120V using 14 awg-- That's about 5%--- again if the load was 10 amps you would have double the lose. It still may be compliant but not a good idea
He will be using motion sensors, he considers them for security. Two 100 watts at each of 3 locations.
Spooky... Dennis guessed the exact load. :blink:
I agree with what others have written re: upsizing the wiring. There is about a 100$ difference between 14-2 UF and 10-2 UF with the length here. Not completely inconsequential for a small job, but if the HO wants more lights later, or an outlet at the last light, how much to retrench that 300' and run #10 or #8 then anyway.
Only You know the job situation. If it was me, PVC conduit with #8 or #6 THHN/THWN & set a 8 circuit panel.
It is interesting how different we all approach the same situation.
My approach would be to make my recommendation to the customer but I have no problem at all installing it exactly how they request it no matter how silly or impractical it might be. Of course within the requirements of the code.
I don't look at it like it is 'my work' it is the person who is paying the bills that owns the work and gets to decide how it is done.
Only You know the job situation. If it was me, PVC conduit with #8 or #6 THHN/THWN & set a 8 circuit panel.