jatindall82

Member
Location
troup, texas
Hey guys I have a question regarding voltage drop in a residential application. I live in Texas, east texas to be exact, and in north Texas #12 nm is the minimum wire size to be used. In east texas we can use #14 for some applications. My question is this, in a house say 6000 square foot your farthest bedroom might be 200 foot away from the panel. In normal instances we run a 14/2 homerun to each bedroom serving the lights (4 recessed cans and a fan) and say 8 plugs. should voltage drop be considered in this application? We have had no problems to date with anything at all going wrong but I was just wondering if this should be brought to the attention of the master over seeing things?
 

peter d

Senior Member
Location
New England
It's a bedroom and chances are a house that large in east Texas, you have a large central A/C system so you aren't going to be using window shakers or space heaters. Not much goes on in a bedroom as far as electrical demand goes. That being said, 200 feet is a long way and I would probably upsize the circuit myself.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
At a 10 amp load you would have 13 volts drop on a #14 at 200 ft taking 120 volts down to 107v.
As peter states, a 10 amp load might be rare in a bedroom but the possibility certainly exists (computer equipment, treadmill). If I invested in a 6000 sq ft home only to find I had a voltage drop problem I would be an unhappy customer which leads to a unhappy builder which leads to a strong possibility of a different electrical contractor.
 

kwired

Electron manager
Location
NE Nebraska
If house is that large that you have 200 foot home runs, maybe one should consider some sub panels in different areas to cut down on home run lengths. If owner/architect don't want that then they can always spend extra $$ on heavier wiring for all the home runs, or give up some performance in voltage drop issues - just be sure to let them know what they are going to get and the consequences that may come with it. If you are in a place that does have minimum rules on VD, then they don't have much choice.
 

JFletcher

Senior Member
Location
Williamsburg, VA
My question is this, in a house say 6000 square foot your farthest bedroom might be 200 foot away from the panel.

Is this a single story house built 200' x 30'?

You could run #12 to the first device then #14 from there, keeping VD down as well as materials cost/labor. There shouldnt be that many home runs that need upsizing - 2, maybe 3? What's 500' of 12/2 NM vs 14/2 NM, $30?

Any chance the panel can be more centrally located?
 

mwm1752

Senior Member
Location
Aspen, Colo
Legal - yes -- pratical - not really -- funny how someone came build a 6000 sq ft home & take the cheapest bids, spend more on carpet than wire. A quality builder will have customers lined up & waiting. A quaility builder will use sub contractors who take care of foreseable issue so they may take credit. Take care of your builder let them know how it really works & most of the time you will benefit from you efforts IMHO.
 

jatindall82

Member
Location
troup, texas
I totally agree with all the comments. I do what I am told at my job. Things like what we are discussing are personal concerns that I take into account so when I do start my own business I am doing the work as I see fit, safe, and just in general what is best for the customer/builder in all aspects. Thanks for your expert opinions and knowledge!!
 