I am working on a new 17,000sq. ft. box store and have an issue with sizing the homeruns. The estimator for the project sized the home runs in 10 AWG. However some of the homeruns are over 250'. The job was priced for utilizing #10 homerun MC cable. My concern is that on some of the longer LED track lighting homeruns that voltage drop may be an issue. The calculated loads average approx. 10 amps at 120 volt.
In order to upsize the homeruns we will have to run EMT which was not figured for the job.
I recall speaking with an engineer we work with that 5% voltage drop for lighting wouldn't be a problem.
Any suggestions or recommendation will be helpful.
Thank you.
In order to upsize the homeruns we will have to run EMT which was not figured for the job.
I recall speaking with an engineer we work with that 5% voltage drop for lighting wouldn't be a problem.
Any suggestions or recommendation will be helpful.
Thank you.