HYPOTHETICAL question . can you run a #12 wire and a #10 wire to a motor 240 v single phase to lower voltage drop ?
HYPOTHETICAL question . can you run a #12 wire and a #10 wire to a motor 240 v single phase to lower voltage drop ?
You only have to run a 10 equipment grounding conductor along the portion of the circuit that has #10 awg. Is that what you meant?Assuming the #12 size is compliant, yes... but you'd have to run a #10 EGC.
If I run # 10 WIRE OR #8 or any size wire to a 8 amp load on a 20 amp breaker I can use #12 wire as a egc if voltage drop is not a issue .
Yes. Wherever #10 is used in the circuit that #12 is the minimum required size. For example, if one line is #12 and one #10 completely from source to motor, the EGC is required to be #10 from source to motor.You only have to run a 10 equipment grounding conductor along the portion of the circuit that has #10 awg. Is that what you meant?
If I run # 10 WIRE OR #8 or any size wire to a 8 amp load on a 20 amp breaker I can use #12 wire as a egc if voltage drop is not a issue .
Well if wire size for voltage drop calculated out to be 11AWG, running one leg in #12 and the other in #10 averages out to running #11, right?I interpreted the question as using a #10 on one leg and a #12 on the other. Why this would be done intentionally or even hypothetically is beyond me. I could see it being done by accident, tho that wouldnt lead to the question op asked
Well if wire size for voltage drop calculated out to be 11AWG, running one leg in #12 and the other in #10 averages out to running #11, right?
Well if wire size for voltage drop calculated out to be 11AWG, running one leg in #12 and the other in #10 averages out to running #11, right?
heh heh
I think the local supply house carries #11, right next to the bin of 24.7A breakers. :lol:
I interpreted the question as using a #10 on one leg and a #12 on the other. Why this would be done intentionally or even hypothetically is beyond me. I could see it being done by accident, tho that wouldnt lead to the question op asked
heh heh
I think the local supply house carries #11, right next to the bin of 24.7A breakers. :lol:
Would improve the voltage drop seen by the motor. Assuming same length on each conductor the amount of drop across the 12 would be higher then across the 10, but the net drop would be less then it would be with 2-12's.I interpreted the question as using a #10 on one leg and a #12 on the other. Why this would be done intentionally or even hypothetically is beyond me. I could see it being done by accident, tho that wouldnt lead to the question op asked
Used to be common to see a reduced size service conductor on high leg of some high leg delta systems where there is limited load connected to the high leg, and if using fused disconnects with properly sized fuse on that leg I see no problem with it. If you OCPD is a breaker - chances are not that great of having a different trip setting on one pole though. Sort of on the same topic with that.I do imagine that being allowed to run different sizes for different phases/polarities of an electrical system would open up a crazy "can of worms" when it comes to applying the concept to three phase systems. But at the same time, I don't see anything in the NEC that would directly prohibit it. You are allowed to run a smaller neutral where it carries less current by the nature of the loads. And in some cases, you may need a larger neutral due to other kinds of loads.
So consider a typical 120V circuit with a #12 and #10 pair of current carrying conductors. If you make the #10 wire the ungrounded one, you'd likely have to have a #10 EGC, and correspondingly a #10 grounded conductor because it has to be at least the same size as the EGC. However, if you run a #10 grounded conductor, it would seem that you could run a #12 ungrounded conductor and a #12 EGC (because EGC sizing is based on the OCPD and the size of the ungrounded conductors). Why would you want to do this, other than as a work-around of an error, I cannot imagine.
If anyone does know why this wouldn't be allowed, please contribute. It doesn't feel like it should be correct to do this.
As expected from the arithmetic mean geometric mean inequality.I get an equivalent 8.02 kcmil when combining #10 and #12 in series, which is less than the Wikipedia value for #11 AWG (8.23 kcmil).