Re: Voltage Drop
1phase or 3phase?
1phase, resistive load:
3% Vd on 480V = 14.4V
R = E/I so R(total) = 14.4V/86A = .167 Ohms
Round trip is 5.6 X 1000 feet so your wire has to be
R(per 1000') = .167 Ohms/5.6 (1000s of feet)
or R(per 1000') = .0299 ohms/1000'
Look at Chapter 9, Table 8 - gives you resistance per 1000'
500Kcmil Cu (uncoated) = .0258 ohms/1000'
Table 9 doesn't exactly apply (it says 3phase). But if you wanted to use it, then per the AC resistance, steel conduit column:
500Kcmil Cu (uncoated) = .029 ohms/1000'
Not much difference for unity pf.
Three phase with an inductive load gets a little whinnier, but still all in your NEC. Look at Chapter 9, Table 9, Note 2. The default table values are for .85pf, which is likely good for general motor loads.
For balanced 3ph, look at the line to neutral (277) Vd. It doesn't matter if the loads are all 480V, or even if you don't have a neutral - answers come out the same. Don't forget the neutral isn't drawing any current, so the distance is just oneway.
3% of 277 = 8.4V
For 2800',
R(per 1000') = 8.4/(86 X 2.8)
= .035 ohms per 1000'
Using Table 9 and the default .85pf:
Steel conduit will require more than 1000Kcmil
750kcmil in PVC conduit is .036 ohms/1000'
1000kcmil in PVC is .032 ohms/1000'
Don't forget, in either case, the grounding conductor has to be upsized the same percentage as the supply conductors were.
Three phase, unbalanced, inductive load, I'll need more information - just send it along with a check and I'll get started. Could take me a while, don't think I've ever done one.
carl