I have a 300' run to a 1/2 horse water well pump to be fed with 240v single phase. With voltage drop I need #6CU conductors. Problem is, #6's will not go under the lugs of the 1/2 HP Franklin motor control which is at the start of the run, nor will they go under the 20A lugs of the 2pole breaker at the panel where the circuit originates. Can I start the circuit at the panel with #12's (20A) for 20' to the Franklin control, go out of the control with 3/#12 +1 ground (for capacitor start), then another 4' to a JB where the #6's start to go underground to the well head? I've wondered before if I can feed larger conductors necessary due to voltage drop on a longer run with smaller conductors starting the circuit, for the same reason each time.