If I have a run of 130' with a breaker rated for 60 amps is it code for me to use 3x #4 thhn because of voltage drop or would I be safe with 6/3 Romex?
limits to voltage drop are typically only required by state building code under the energy conservation chapter. most plans reviewers won't pick up on it. for Florida, its 5% max branch+feeder.If I have a run of 130' with a breaker rated for 60 amps is it code for me to use 3x #4 thhn because of voltage drop or would I be safe with 6/3 Romex?
Verifying your suspicion.The only nec article that has a voltage drop requirement is 695 fire pumps ( disclaimer, may be requirement in COPS article, which most have never used or even read)
There is one in 647.The only nec article that has a voltage drop requirement is 695 fire pumps ( disclaimer, may be requirement in COPS article, which most have never used or even read)
647.4(D) Voltage Drop.
The voltage drop on any branch circuit shall not exceed 1.5 percent. The combined voltage drop of feeder and branch-circuit conductors shall not exceed 2.5 percent.
HAH! There are actually sixteen mentions, easily found using the "NFPA Link" search function. For $99/year I'm a believer!There is one in 647.
There may be another.