Sajid khan
Senior Member
- Location
- Pakistan
Measured voltage drop thru calibrated fluke analyzer is occuring too much high as compare to calculated voltage drop.
What could be possible reasons; negative Ferranti, Aged cables, power factor or any other possible reason???
Analyzer reading on 2 sets 240 1C PVC/PVC: 115 Amps ,372 Volts at 260 meters..
The calculated VD at 400V is 3V only while the actual measured at analyser is 28V.
The load is being by a generator.
Sent from my iPhone using Tapatalk
What could be possible reasons; negative Ferranti, Aged cables, power factor or any other possible reason???
Analyzer reading on 2 sets 240 1C PVC/PVC: 115 Amps ,372 Volts at 260 meters..
The calculated VD at 400V is 3V only while the actual measured at analyser is 28V.
The load is being by a generator.