Is there a different calculation or criteria I need to consider when calculating voltage drop for a PV system.
I have a meter 545ft from a SWB
2 PV inverters approximately 90ft
2 PV inverter’s approximately 60
2 PV inverters approximately 40 From the SWB. Each inverter circuit has an OCPD of 175 amp
AC is 480v 3phase
The engineered values are
5-runs of 600kcmil AL from meter to the SWB
90ft inverters 350kcmil 3phase
60ft inverters 300kcmil
40 ft inverters 250kcmil
20ft inverters 4/0awg
All conductors are AL.
My primary question is do I add the cumulative VD from the meter out to inv 90ft
Does VD calc reset at any point is there any special condition I need to be cautious about?
Thank you
I have a meter 545ft from a SWB
2 PV inverters approximately 90ft
2 PV inverter’s approximately 60
2 PV inverters approximately 40 From the SWB. Each inverter circuit has an OCPD of 175 amp
AC is 480v 3phase
The engineered values are
5-runs of 600kcmil AL from meter to the SWB
90ft inverters 350kcmil 3phase
60ft inverters 300kcmil
40 ft inverters 250kcmil
20ft inverters 4/0awg
All conductors are AL.
My primary question is do I add the cumulative VD from the meter out to inv 90ft
Does VD calc reset at any point is there any special condition I need to be cautious about?
Thank you