Voltage drop

Status
Not open for further replies.

Obed.T29

Member
Location
Dallas Texas
Occupation
Electrician
Hello I’m having issues with de rating here
Engineer wants :
0- 75ft
4-6 CCC’s =12 awg
7-9 CCC’s = 10 awg
10-20 CCC’s =8 awg

•75’-150
4-6= 10 awg
7-9= 10 awg
10-20= 8awg
•150’ +
4-6= 8awg
7-9= 8awg
10-20=8awg

There’s 1” emt
5 20amp 10awg circuits = 10 ccc’s
1 15 amp 240 10 awg = 2 ccc’s
This is a multifamily
 
Looks like he derates using the ampacities in the 90°C column and the adjustment factors from 310.15(B)(3)(a). In your 1" EMT, the 10awg has a starting ampacity of 40A. With 12 CCC's, the adjustment factor is 50%, so you're good for 20A circuits, and certainly good for 15A.

My question is why is all this in one pipe, and not NM cable?
 
Looks like he derates using the ampacities in the 90°C column and the adjustment factors from 310.15(B)(3)(a). In your 1" EMT, the 10awg has a starting ampacity of 40A. With 12 CCC's, the adjustment factor is 50%, so you're good for 20A circuits, and certainly good for 15A.

My question is why is all this in one pipe, and not NM cable?
It’s a take over job. Engineer is also accounting for 3% voltage drop which is why they mention 8 awg.
 