Not sure if I'm calcuting this correct for primary(277/480v) side.
Have RGS conduit and copper XHHW wire going from a 100AF/70AT breaker in switchboard 850' to 70A enclosed breaker and then primary side xfrmr.
They are saying to run 3#350 & #3/0. Seems oversized. I come up with 4/0 to keep under 3% VD.
BTW when plugging in valued to VD calcutor how would I know whether to use 277 or 480v? Thanks