Voltage Drop

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Not sure if I'm calcuting this correct for primary(277/480v) side.

Have RGS conduit and copper XHHW wire going from a 100AF/70AT breaker in switchboard 850' to 70A enclosed breaker and then primary side xfrmr.

They are saying to run 3#350 & #3/0. Seems oversized. I come up with 4/0 to keep under 3% VD.

BTW when plugging in valued to VD calcutor how would I know whether to use 277 or 480v? Thanks


1730336525442.png
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If I use NEC Table 9 [Effective Z for steel conduit] I get for 1/0 2.79% drop.
 

PD1972

Member
Location
New York (2017 NEC)
Occupation
engineer
It looks like the transformer is going to be 45kVA, so I would use 54A at 480V for the calculation.

Based on the 350kcmil (at copper) the drop at full load of the transformer is ~1%VD. Is that what the designer is trying to do by leaving 4%VD for everything fed from that panelboard?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
It looks like the transformer is going to be 45kVA, so I would use 54A at 480V for the calculation.

Based on the 350kcmil (at copper) the drop at full load of the transformer is ~1%VD. Is that what the designer is trying to do by leaving 4%VD for everything fed from that panelboard?
Forgive my "stupid" but I don't understand that.....
the transformer appears to be the only load on the 480 v feeder and if he keeps that to 3% at full current that should not affect the panleboard load should it ??
 

PD1972

Member
Location
New York (2017 NEC)
Occupation
engineer
Forgive my "stupid" but I don't understand that.....
the transformer appears to be the only load on the 480 v feeder and if he keeps that to 3% at full current that should not affect the panleboard load should it ??
Total allowable combined VD between feeder and branch circuit per adopted state energy codes I am familiar with has been 5%.

OP mentions the feeder is coming from a switchboard, which I am assuming to be the service. You can definitely keep the feeder VD to 3% between switchboard and transformer as it wouldn't technically affect panelboard loads; however, branch circuit conductor sizes of circuits fed from the panelboard may be larger to achieve a 2% branch circuit VD.

A 1% feeder VD between switchboard and panelboard would allow for branch circuit conductor sizes to be sized to 4% max VD. I do not know if the increased cost in a larger feeder would offset the cost of larger branch circuit conductors, but that is (in my opinion) what would drive the decision.
 