As far as I know the NEC does not have an allowable Vd.This Mike holt video has controversy. Between nec allowable voltage drop...
Only for a couple of specific cases, fire pump motors (695.7) and sensitive electronic equipment [647.4(D)].As far as I know the NEC does not have an allowable Vd.
The code does not require that circuit conductors be sized to reduce voltage drop. That has been said more than once, so how is your question not answered. You can size the circuit anyway that you want too, as long as the rating of the OCPD does not exceed the ampacity of the conductor.None of this answered my question. Watch his video first
He saying that you have to comply with the manufacturer's instructions which under ANSI is between -10% to +5 compared to nominal voltage. I know of no one who is enforcing that based on 110.3.None of this answered my question. Watch his video first
Ok so basically if your v drop for any circuit exceeds 3% then you adjust wire size accordinglyHe saying that you have to comply with the manufacturer's instructions which under ANSI is between -10% to +5 compared to nominal voltage. I know of no one who is enforcing that based on 110.3.
Not really, if your starting voltage is 115 volts and down the street your starting voltage is 125 volts how does a generic percentage work?Ok so basically if your v drop for any circuit exceeds 3% then you adjust wire size accordingly
No not if you're sizing according to the video. He said in the range of -10% from nominal to +5% from nominal.Ok so basically if your v drop for any circuit exceeds 3% then you adjust wire size accordingly
Ok not the video I’m taking real world that’s the whole purpose of the questionNo not if you're sizing according to the video. He said in the range of -10% from nominal to +5% from nominal.
Not really, if your starting voltage is 115 volts and down the street your starting voltage is 125 volts how does a generic percentage work?
Down the street? Huh I’m talking if I was at a buildings nominal voltage was 120/208 1 outlet they need is 300 feet away. I do calculations to size wire based on not dropping over 3% Right?Not really, if your starting voltage is 115 volts and down the street your starting voltage is 125 volts how does a generic percentage work?
Disregarding Mike's video in the real world the VD percentages in the NEC are merely suggestions. If you feel that it's a better job to provide VD compensation then that's fine you may do so. If the building system is 208Y/120 then use those numbers in your calculation.Ok not the video I’m taking real world that’s the whole purpose of the question
What is the voltage rating of the equipment that will be connected to the circuit?Down the street? Huh I’m talking if I was at a buildings nominal voltage was 120/208 1 outlet they need is 300 feet away. I do calculations to size wire based on not dropping over 3% Right?
Suggestions? So in regards to VD, a 20a circuit single outlet installed 300 feet from the breaker can be ran in #12 because VD is a suggestion? You’d get Like 80v at the device so come on?Disregarding Mike's video in the real world thew VD percentages in the NEC are merely suggestions. If you feel that it's a better job to provide VD compensation then that's fine you may do so. If the building system is 208Y/120 then use those numbers in your calculation.
Yea no one knows they just want an outlet how bout now?What is the voltage rating of the equipment that will be connected to the circuit?
You can but not required. So, let me try again, you are at a building and the service voltage is 120 volts, you are going to add a receptacle 300' away from the service, then a customer calls from down the street and wants a receptacle added 300' from their service but their service voltage is 115 volts, how does one size fit both?Down the street? Huh I’m talking if I was at a buildings nominal voltage was 120/208 1 outlet they need is 300 feet away. I do calculations to size wire based on not dropping over 3% Right?
you’re loosing my point with this. WhyYou can but not required. So, let me try again, you are at a building and the service voltage is 120 volts, you are going to add a receptacle 300' away from the service, then a customer calls from down the street and wants a receptacle added 300' from their service but their service voltage is 115 volts, how does one size fit both?
It is a design issue, not a code issue.Yea no one knows they just want an outlet how bout now?