I wired a 2400 sq ft house last year. I ran 4/0 au 240' to a 200 amp 42 space panel. Home owner called yesterday complaining that the lights are dimming when the ac comes on. Ac is pulling 35 amps coming on and about 20amps running. I ran #6 copper about 60' for the ac. I had the homeowner turn on ac, hot water heater, stove, and all lights and fans. The load in the panel was about 110 amps. If I calculated right the service load came out to 102 amps when I was sizing the service when I bid it. Anyway voltage is 246v at meter and 231v at the panel with a load of 110 amps. I don't understand why I'm getting 15v drop. According to this calculation wire should be oversized.
2 X 21.2 appr.K X 250' X 110amps/ 12 (vd per) = 97,166 = 1/0 (105,600)
What am I missing here? Homowner has had 2 ref. motors burn out in the last year.
I know it's a long distance to the house but the calc. takes that into consideration. It's also another 200' from the meter to the transformer. Overhead service. I'm not sure what size of triplex. Taking a swag it looks like 2/0 from the ground.
If anyone could help me out here I would appreciate it.
2 X 21.2 appr.K X 250' X 110amps/ 12 (vd per) = 97,166 = 1/0 (105,600)
What am I missing here? Homowner has had 2 ref. motors burn out in the last year.
I know it's a long distance to the house but the calc. takes that into consideration. It's also another 200' from the meter to the transformer. Overhead service. I'm not sure what size of triplex. Taking a swag it looks like 2/0 from the ground.
If anyone could help me out here I would appreciate it.