puckman
Senior Member
- Location
- ridgewood, n.j.
i should know this problem but i don't . there is this service 208volt 3 phase,
the highest reading i get is 200v lowest is 198v. i have an ac unit 175' away
and the voltage at unit when running is 187v., the unit has been in service for years and just started to tripout. ac unit is wired with #10 solid in a 3/4 " emt with 8 # 12 in conduit and i plan on changing to #8 mc. my question is do i have power co. problem
or is 200volts reading standard? the ac uses 197v to 240v .
thanks for your replys.