tommy said:Can I get example on how and when to use 3% and the 5% for VD
3%--- --------tommy said:So if I was installing just the main feeder I would use What? ( 1%thru to 5% mychoice?
Ruwired got it right. If you run a feeder you calculate the VD at 3%. We generally never calculate the VD from the feeder thru the branch circuit. Normally we would do the feeder at 3% and then the branch circuits at 3%. Technically you should do the feeder plus the branch circuit at 5%Dennis Alwon said:3%--- --------
Snorks said:Title 24 refers to Energy Efficient specifications and always have lesser VD allowances.
tommy said:George why do think its not required.I agree FPN is not enforcible, But why have it there?Just curious on any thoughts.Maybe should be required,maybe too hard to inspect or something
2-277 Log #2837 NEC-P02 Final Action: Reject
(215.2(A)(3), FPN 2)
______________________________________________________________
Submitter: Robert P. McGann, City of Cambridge
Recommendation: Make this Fine Print Note into mandatory text.
Substantiation: This is necessary to properly facilitate the operation of overcurrent protection. We are all looking at ways to reduce the number of electrical fires. This will aid us in achieving that goal.
Panel Meeting Action: Reject
Panel Statement: Acceptable voltage drop is a system design issue that may vary with the application and equipment involved.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12