sparkease said:using a 1 phase circuit at 208 volts is the length of wire used to figuire v. drop twice the linear distance from source to load. load in this case being 20 amps at 600 linear feet or total conductor lenght 1200 feet using length out and back.
Using 208 or 240 volts, you only use the distance one way. If the voltage is 120 volts, you have a return on the neutral so you use 2 x the distance.sparkease said:using a 1 phase circuit at 208 volts is the length of wire used to figuire v. drop twice the linear distance from source to load. load in this case being 20 amps at 600 linear feet or total conductor lenght 1200 feet using length out and back.
The online formula I linked to shows one way either scenario. I know there is more than one way to figure VD but....bob said:Using 208 or 240 volts, you only use the distance one way. If the voltage is 120 volts, you have a return on the neutral so you use 2 x the distance.