Re: Voltage Drop
All of the formulas discussed above provide approximate values for voltage drop. The approximation is considered ?good enough? for the purposes of ?code compliance.? Actually, that?s not hard, since there is no NEC requirement, only a vague hint, relating to voltage drop.
Using the value of 26.4, as compared to 25.8 (i.e., 2 times a K value of 12.9), would give also an ?approximate value,? but it will be higher (by about 2%) than that use by most of the industry. It would be conservative (i.e., would be safe), but it might lead you to base your bid on a cable that is one size larger than your competitor will be using.
But now to mathematics. To say that ?K is 12.9? is to use the ?Approximate K Method? of voltage drop. The ?Exact K Method? requires you to calculate a value for K, based on information in Table 8. The formula is: K = (R * CM) / 1000, where R is the tabulated resistance (in ohms per 1000 ft) and CM is the area in circular mils. I created a quick spreadsheet using both Uncoated Copper and Coated Copper, and looking at stranded and un-stranded (up to size 8) conductors from sizes 18 to 500 MCM. I calculated ?Exact K? values ranging from 12.6 to 12.9 (Uncoated Copper) and from 13.0 to 13.7 (Coated Copper). I found an ?Exact K? of 13.2 (corresponding to the 26.4 of Rudy V?s formula) on Coated 4/0 and Coated 400 MCM.