When calculating for voltage drop on branch circuits, do you calculate the furthest outlet at **va x the length from the panel? or from the next closest outlet in the run to the panel?

i.e. outlet at 180va------25'-----outlet------25'-----outlet-------150'---panel.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
jwest78 said:
When calculating for voltage drop on branch circuits,

It would be the total resistance of the circuit, IOW's, from the panel to the last load.