I have lighting circuit that has 13 -2x4 fixtures on it . The first fixture is 180 feet from the panel. Then there is 8 feet between each fixture. I'am sharing a nuetral for two circuits. The service is 3phase 208v. That would make it about 280 feet to the last fixture. I used the voltage drop calculator with the worst case scenario 10.5 amps at the end and it came to 8 wire. I believe that if i knew how to calculate at each fixture that 10 wire might make it. ??