Does the NEC anywhere define "voltage drop" and specifically, how is it measured?
I am told by an electrical contractor that voltage drop is not measured under load. As an engineer, this flies in the face of my training.
The application is a new single family residence. Supply voltage (Measured at the service entrance with a calibrated digital voltmeter.) is 127VAC. Voltage at furthest outlet from panel (130 feet) is 123 VAC.
Both of the above with no load.
This same outlet under load (1800 watts) measures 114VAC. I feel there is a problem with undersized wire, defective connection, or?
Can anyone refer me to appropriate sections of NEC which apply? Many Thanks jj19897