Voltage drop
arnettda
vd=1.732xkxIxD
___________ I know VD so I end up with 4% = 2234.28 X I
__________
CM 133100
I do not remember how to cross multiply and divide? Or how do I end up with the right answer?
And If I know v =480 volts and I measure 464 v when machine is running can I assume my volt drop is 4%.
This current rating will change with my increas in wire size?
vd=1.732xkxIxD
__________
CM 133100
Multiple spaces get stripped out. If you want spaces, use "......" and change the color to white like th...is.
It is not "%" = # x I it is "voltage drop" = # x I
the % is "voltage drop" / Source voltage
1-464/480 = 3.33% drop or VD=16
So using the method you used:
vd = 16 = 1.732 x K x I x D / Cmil
I = (16 x Cmil) / (1.732 x K x D)