We are installing a few pole lights. The lights are 150w each and there are three lights. The power is 208v. The distance is 400' and we were planning on running #10. The plans call for #4. Am I out of line thinking this is overkill? The load will draw just over 2 amps. Their logic is that the circuit will have a 20a breaker so the voltage drop should be calculated on a 20a load. I suggested we could solve that problem (which I don't even consider a real problem) by using a smaller breaker, fusing etc.
Upsizing to #4 for some POSSIBLE future load that isn't in any kind of plan for the foreseeable future seems a little crazy to me. There is plenty of room to do another pull in the future if they do add another load.