whats the voltage drop for 11kw range with #12thw at 225 ft.?
whats the voltage drop for 11kw range with #12thw at 225 ft.?
I would say unless you are running this range at 550 or more volts that it is a moot point as 11 KW at 240 is 45 amps.
That 12 AWG is going to be a bit warm.
are you paralleling the #12's???
Wouldn't that be illegal? 310.10(H)(1)
(H) Conductors in Parallel.
(1) General. Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded circuit
shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger where
installed in accordance with 310.10(H)(2) through (H)(6).
Jason are you a contractor? Are you doing this as a side job?whats the voltage drop for 11kw range with #12thw at 225 ft.?
It was an attempt at humor based on the information provided. the only he can supply an 11KW load with #12 is if he uses multiple sets.