A property owner (who thought he was doing himself a favor) installed over 200 feet of 1 1/4 SCH 40 from his residence to a detached garage that as built a few months ago. The voltage drop, however, if we use 2 AWG for a 100 A subpanel, would be close to 6%.
Sizing wire to keep Vd to 3% would require 2/0 - which isn't happening in 1 1/4 SCH 40
I had another electrical contractor tell me it should be ok to run he 2 AWG in spite of the voltage drop.
Any input would be much appreciated.
Thanks, Jemsvcs