Went to a mobile home, customer wanted to ad 3 dedicated receps in a room being used as an office. Room had 3 cpu's and one larger copy machine, one laser printer, one fax machine, and a ups for the cpu's. I was told that the lights keep dimming periodically, and sometimes the power in the room flickers. No breakers tripping, I checked voltage on a recep in the room and sure enough the voltage held at 120v then when the lights dimmed about every minute or so the voltage would drop to 111v.
L-N voltage 120
L-G voltage 120
N-G voltage 2.4volts
I'm thinking possible loose connection or nicked wire leaking voltage under load. No load seemed to be kicking on and off, just the lights would flicker every min or so. I checked for the voltage drop at the service and there was no drop at all.
What have you found to be the cause of a problem like this?... could it just be all the cpu equipment and maybe the circuits should have a super neutral?