Just got back from a service call where the original symptom was flickering lights. I went to the house and observed the flickering, and it pretty much affected every light in the house. It was more pronounced when the coffee pot and crock pot were plugged in.
What surprised me, though, was that the circuits were fairly well balanced. The lights throughout the house were split among several circuits, and the kitchen receptacles were on a circuit separate from the lights. Nothing in the house drew much current. It had 100A service, and I measured 3.5A on one leg and 5.5A on the other.
Then I discovered that the voltages were not consistent. H-N on one leg at the panel varied between 110V-114V, and the other showed 126V-130V. H-G was consistently 120V on both legs. Neutral and ground were not tied together in the panel because there was an outside disconnect switch (fuses) between the panel and the meter socket. The same readings showed up inside the disco switch and on the line and load side of the meter. But these readings all go to normal if I shut off the main in the panelboard.
My thinking is that there's loose neutral somewhere upstream of the panelboard lugs or degradation of the insulation on one or more of the service-entrance wires. I'm leaning toward the loose-neutral theory since H-G is always 120V. I didn't see anything that looked problematic, though. Everything I looked at was in good shape, lugs were nice and tight, no obvious wire damage, etc.
If anyone has any other ideas, I'd be happy to hear them.
What surprised me, though, was that the circuits were fairly well balanced. The lights throughout the house were split among several circuits, and the kitchen receptacles were on a circuit separate from the lights. Nothing in the house drew much current. It had 100A service, and I measured 3.5A on one leg and 5.5A on the other.
Then I discovered that the voltages were not consistent. H-N on one leg at the panel varied between 110V-114V, and the other showed 126V-130V. H-G was consistently 120V on both legs. Neutral and ground were not tied together in the panel because there was an outside disconnect switch (fuses) between the panel and the meter socket. The same readings showed up inside the disco switch and on the line and load side of the meter. But these readings all go to normal if I shut off the main in the panelboard.
My thinking is that there's loose neutral somewhere upstream of the panelboard lugs or degradation of the insulation on one or more of the service-entrance wires. I'm leaning toward the loose-neutral theory since H-G is always 120V. I didn't see anything that looked problematic, though. Everything I looked at was in good shape, lugs were nice and tight, no obvious wire damage, etc.