voltage fluxuation

Status
Not open for further replies.

ceb58

Senior Member
Location
Raeford, NC
OK need ideas. 25kw Generac gen. set. When the load is transferred to gen. the voltage starts fluctuating 215-250v L-L .With out load it holds 242v with no change. My first thought was loose connection checked termination in ats, good. Connections in disco. was able to get about 3/4 of a turn on all terminals. Tried it again same thing. Was going to check terminations on breaker in gen. set but it started raining like crazy. There is also a 12kw UPS on this system. I opened the main breaker to isolate the UPS from the system and it made no difference in the fluxuation. I ohm'ed all wireing out nothing. The only thing I found strange was at the gen. disco the contractor installed. The gen. set has a 125amp breaker the contractor installed a 200amp rated fusible disco. with 200amp fuses. I could read .83 ohm's L-L at the disco. My thought now is the voltage regulator. Any other ideas?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Achmed, does the engine itself vary in speed as well? Have you checked the output frequency?

Have you checked the running voltage at the generator itself? That would eliminate most of the installation quickly.

I have seen a 7kw Generac hunt (vary in speed) if too-lightly loaded.
 

RESI

Member
Location
Virginia
ceb58

Ziller Electric has a forum for Generac generators. Just google Ziller Electric and it should lead you to the forum.
 

ceb58

Senior Member
Location
Raeford, NC
Achmed, does the engine itself vary in speed as well? Have you checked the output frequency?

Have you checked the running voltage at the generator itself? That would eliminate most of the installation quickly.

I have seen a 7kw Generac hunt (vary in speed) if too-lightly loaded.

By the display the Hz are not fluctuating, the engine (diesel) is maintaining a Constance speed. The amp draw on the building is in the 50-60 amp range. This is why I isolated the UPS from the system we have had some that the UPS kw to gen. kw ratio would make the gen set go stupid.
I will go back next week to get to the breaker to check voltage could not do it yesterday due to it raining cats and dogs.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Larry
Are you suggesting the gen is an inverter type? Otherwise the engine speed and the gen frequency are sort of locked.
Inverter, no. I expected the speed/frequency relationship, which is why I asked.

By the display the Hz are not fluctuating, the engine (diesel) is maintaining a Constance speed.
Then it's not mechanical, and thus must be electrical or electronic. If the phase-to-neutral voltages are equal, it's likely not electrical, and thus must be electronic.

I suspect a voltage-regulator issue.
 