ceb58
Senior Member
- Location
- Raeford, NC
OK need ideas. 25kw Generac gen. set. When the load is transferred to gen. the voltage starts fluctuating 215-250v L-L .With out load it holds 242v with no change. My first thought was loose connection checked termination in ats, good. Connections in disco. was able to get about 3/4 of a turn on all terminals. Tried it again same thing. Was going to check terminations on breaker in gen. set but it started raining like crazy. There is also a 12kw UPS on this system. I opened the main breaker to isolate the UPS from the system and it made no difference in the fluxuation. I ohm'ed all wireing out nothing. The only thing I found strange was at the gen. disco the contractor installed. The gen. set has a 125amp breaker the contractor installed a 200amp rated fusible disco. with 200amp fuses. I could read .83 ohm's L-L at the disco. My thought now is the voltage regulator. Any other ideas?