KamilAussie
- Czech Republic
If the center points of the Y's are connected, Us = UosHi, I have a 3 phase symetric (230/400 V) circuit, Y-Y configuration as shown in the picture.
Could anyone tell me how to calculate voltage Ur or Us?
I don´t know how to start without knowing the exact value of Z.
Thank you :angel:
If you are trying to figure out the currents you need to know Z.
If all you are concerned about are the voltages you will find that the value of Z cancels out when solving the equations.
If the center points of the two wyes are not connected and the magnitudes of the three leg voltages are not equal the analysis gets a little more complex, but is still doable.
Apply Kirchoff's Laws.
The total current at the center point of the load wye must be zero.
mobile