Voltage Line or Phase Voltage
BatmanisWatching1987
NJ
Jr. EE
How do you determine if the voltage in a given problem is Line or Phase Voltage given unless otherwise stated.
Here is an example
"A three phase, 230 kV transmission line has a reactance of 50 ohms per phase and aresistance of 10 ohms per phase. The current per phase is 100 amps. What are the total active
power losses in the transmission system?"
Disclaimer - I don't do transmission lines (except for the one on the PE test) Translation - I may be all wet.
Here is an example
Assumption: This is a PE practice problem. Because if it were life, you would know.
Unless specified otherwise, the voltage will be line to line.
Curiosity Q: For this problem why would it matter?
I also thought it was VL but it was actually VP
Since I was trying to first find the Vdrop, then use S3P = sqrt(3)*Vdrop*I to find he value for P+jQ
But I needed to use the formula S3p=3*Vdrop*Ip to get the correct answer
According to my EE friend, a transmission line voltage always refers to the line-to-line voltage.
Adding to gar's post: Yes, you do need to work the power per phase. Cause there is real power lost in each phase. But the V(L-L) or V(P-N) don't have any thing to do with it.
Or you could use P = Real(3*(I^2)*Z) The vars don't count.
If this is a PE test practice, I highly suggest you purchase the solutions manual.
Okay - So why did you ask?
the worm
the worm
I thought it was VL but it was actually VP. Hence why, I was wondering if I missed read the problem knowing it was actually VP given.
I initially used P=3*I2*Z but then I wanted to check my answer but I got 2 different answer when I used S3P = sqrt(3)*Vdrop*I
190313-2434 EST
Batman:
From your last post I am not sure that you clearly, intuitively, understand the question, assumptions, and the solution.
Here is an example
Voltages are always expressed as line values unless specified otherwise. The nature/context of the problem will usually be obvious if they referring to line-to-neutral or line-to-ground values.
Here is an example
This is a poorly written problem. It should either give you the line current or specify whether the load is Y or Δ. Line voltage is irrelevant here.
Disclaimer still in effect
It is line loss, VL, VP doesn't matter. As you note, Vdrop does.
Consider:
Power dissipation in each phase conductor = Vdrop*I​
(sqrt(3) is not part of this) The only things that matter are the phase conductor current and the Voltage drop on that conductor.​
Vdrop = I*Z
Substituting
Complex Power(each phase conductor) = (I*Z)*I = I^2*Z
But you only want the real part
P = Real(I^2*Z)
Total power dissipated = 3*P​
Still curious:
Q1: How is it you know the "230KV" was VP, and not VL?
Q2: Why Would it matter?
The Worm (turneth and begins to dig)
Agreed. What is important is the current, the impedance, and the voltage drop. The voltage itself isn't relevant. Just because information is given in a problem setup, that doesn't mean it is needed to solve the problem.
Perhaps he wanted to crosscheck?
190314-1254 EDT
In looking at this question --- it was very well designed and written.
It provided sufficient information for one to solve the problem without having to make assumptions, and it provided enough additional information to confuse one that did not really understand the subject and problem.
Crosscheck what? The voltage doesn't enter into any of the equations. The differential voltage does, but that's just voltage drop.
When there is information in a test problem that is ambiguous, e.g., the voltage in a transmission line is given but it isn't clear whether it's phase to neutral or phase to phase, that's a pretty strong clue that the information isn't needed to solve the problem.