Hello,
I'm installing a 100kW PV array on a building with a 120/208 service. It's less expensive to use inverters with a 480/277 output and a transformer than it is to use 208v inverters. So we energized the system today and all the voltage and resistance readings on the primary (building/208 side) of the transformer are correct. However, I got some strange voltage readings on the secondary (solar/480 side): Phase to neutral is 277v, phase to phase is 480v, Phase to ground is 180V, neutral to ground is 15v. I've attached an image of the line diagram.
The transformer doesn't say that it's a neutral isolating type, but I think it may be based on the voltage readings. If I understand correctly, an isolating transformer is treated as a separately derived system, which would call for a new neutral-ground bond on the secondary side of the transformer.

I'm installing a 100kW PV array on a building with a 120/208 service. It's less expensive to use inverters with a 480/277 output and a transformer than it is to use 208v inverters. So we energized the system today and all the voltage and resistance readings on the primary (building/208 side) of the transformer are correct. However, I got some strange voltage readings on the secondary (solar/480 side): Phase to neutral is 277v, phase to phase is 480v, Phase to ground is 180V, neutral to ground is 15v. I've attached an image of the line diagram.
The transformer doesn't say that it's a neutral isolating type, but I think it may be based on the voltage readings. If I understand correctly, an isolating transformer is treated as a separately derived system, which would call for a new neutral-ground bond on the secondary side of the transformer.