Voltage on Breaker

Status
Not open for further replies.

Hfalz1

Member
Location
Houston, Tx.
Occupation
Electrician
Why am i getting 9.0V on a breaker that is off in a 3 phase panel? Single pole 20A. Only 4 receptacles on the circuit. Nothing plugged into them no load.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
As others stated. Most likely “ghost voltage”. If your In the profession of trouble shooting a decent amount get your self a fluke 117 or something with low impedance mode (LowZ).

Got one several years ago and absolutely love it.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
Adding a load at the test points will drop the voltage. Sometimes just another tester.

We used Fluke T+Pros so we all had the same information when testing. IDR the exact circumstances now but we didn't trust what one tester was showing us. Adding a second, then third dropped the voltage each time.
 

MD Automation

Senior Member
Location
Maryland
Occupation
Engineer
Only 3 circuits in one conduit. ABC phase with neutrals and one ground.
Like others have indicated - likely "ghost" voltage.

You say there are 3 phases in the same conduit. And the breaker you are measuring at is one of these phases? But the other 2 are hot?

If so, then you have 3 wires (2 of them hot) running all alongside each other for however long the conduit run is. This makes a really crummy, but still legit, capacitor - and the dead phase just shows up with a small capacitively coupled voltage because it's in the vicinity of the other 2 hots for a long enough length.

You can only measure this with a high impedance meter - because it introduces no load on that leg to drag it down. That ghost voltage will likely disappear the instant you load the circuit with just about anything (except LEDs ;)). Try plugging in a small incandescent bulb in see what happens to the 9 volts.
 

zooby

Senior Member
Location
Indiana
Occupation
maint. electrician
As others stated. Most likely “ghost voltage”. If your In the profession of trouble shooting a decent amount get your self a fluke 117 or something with low impedance mode (LowZ).

Got one several years ago and absolutely love it.
Would clamp meters (fluke 374, 375, 376) be high impedance or? Thanks.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
This is why the electronic breakers trip ... "Phanton." voltage.

See my proposal for update to NEC.
 