Hfalz1
Member
- Location
- Houston, Tx.
- Occupation
- Electrician
Why am i getting 9.0V on a breaker that is off in a 3 phase panel? Single pole 20A. Only 4 receptacles on the circuit. Nothing plugged into them no load.
Like others have indicated - likely "ghost" voltage.Only 3 circuits in one conduit. ABC phase with neutrals and one ground.
Would clamp meters (fluke 374, 375, 376) be high impedance or? Thanks.As others stated. Most likely “ghost voltage”. If your In the profession of trouble shooting a decent amount get your self a fluke 117 or something with low impedance mode (LowZ).
Got one several years ago and absolutely love it.
Without looking into them and been a while since I had a 375/376. I would say they are most likely high impedance meters.Would clamp meters (fluke 374, 375, 376) be high impedance or? Thanks.
Are they that old?Without looking into them and been a while since I had a 375/376. I would say they are most likely high impedance meters.
very cool---well ok helpful---Thanks very much.As an educational reference, here is a NEMA bulletin
YepI use a solenoid tester for troubleshooting, and a voltmeter only when I need to know the exact voltage.
View attachment 2563842