Matt Harless
Member
- Location
- Loudon, TN
- Occupation
- GC
Not an electrician. I'm a GC who helps my electrician when he needs it. So far, everyone is at a loss to explain my situation.
Here it is:
My family two months ago moved into a 50ish year old home. Yesterday, while checking the water pressure at an outside spigot, my 17yo son got a mild shock. He had apparently gotten somewhat wet enough to get a good earth connection. He was about 50' from the service entrance at the time. I was away so he stuck a meter in the ground(physical earth) and checked voltage on the spigot. Got as high as 40v. Varied a lot and would seem to ramp up and down slowly sometimes and other times it would jump up or down. Holds at ~20v most of the time. (as a side note, some of my plumbing is pex, some galvanized. Water heater is in the pex portion. Galvanized portion is bonded)
Called the poco, they come out and are not able to explain it. We went from maybe a bad meter, to maybe issue with transformer, and on and on. At one point they were pointing the finger at my main breaker(it is original to the house) which makes no sense to me. They were great guys, some of them not on call and still staying late at my house on Friday. We had half the company here I think, but they just had no solution.
They took all hots loose from the house, and still had voltage on the neutral. I think it was 16v at that point. Drove some ground rods, replaced the service entrance to the weatherhead, replaced the transformer, recrimped connections on various poles leading up to the house. At this point with all of that changed and nothing connected but neutral at the pole, we can read 7-10v on the ground of the house. With line voltage connected, we are getting ~12-15v to earth via the spigot.
I was reading 13v in the shower of my house from water to drain which is concerning so i removed the bond to the galvanized. It is still getting some somewhere though because there is 2v potential still in the shower.
Does anyone have any ideas? I cannot imagine a scenario where the issue is on my side but if it is that would be great and we could just get the electrician to fix it.
Also, I have 6 kids, how concerned would you be about staying in the house.
Thanks
Here it is:
My family two months ago moved into a 50ish year old home. Yesterday, while checking the water pressure at an outside spigot, my 17yo son got a mild shock. He had apparently gotten somewhat wet enough to get a good earth connection. He was about 50' from the service entrance at the time. I was away so he stuck a meter in the ground(physical earth) and checked voltage on the spigot. Got as high as 40v. Varied a lot and would seem to ramp up and down slowly sometimes and other times it would jump up or down. Holds at ~20v most of the time. (as a side note, some of my plumbing is pex, some galvanized. Water heater is in the pex portion. Galvanized portion is bonded)
Called the poco, they come out and are not able to explain it. We went from maybe a bad meter, to maybe issue with transformer, and on and on. At one point they were pointing the finger at my main breaker(it is original to the house) which makes no sense to me. They were great guys, some of them not on call and still staying late at my house on Friday. We had half the company here I think, but they just had no solution.
They took all hots loose from the house, and still had voltage on the neutral. I think it was 16v at that point. Drove some ground rods, replaced the service entrance to the weatherhead, replaced the transformer, recrimped connections on various poles leading up to the house. At this point with all of that changed and nothing connected but neutral at the pole, we can read 7-10v on the ground of the house. With line voltage connected, we are getting ~12-15v to earth via the spigot.
I was reading 13v in the shower of my house from water to drain which is concerning so i removed the bond to the galvanized. It is still getting some somewhere though because there is 2v potential still in the shower.
Does anyone have any ideas? I cannot imagine a scenario where the issue is on my side but if it is that would be great and we could just get the electrician to fix it.
Also, I have 6 kids, how concerned would you be about staying in the house.
Thanks