Voltage on led lighting circuit

John165

Member
Location
New Mexico
Occupation
Journeyman
We just finished a job, large metal garage, & were checking voltage, when something interesting happened. With the lights on the voltage was 124.6v, with the lights off it was 120.8v. The only thing I can think of is the drivers back feeding or something like it. Is this a common or is there something wrong? We have about 1600 watts on the circuit, the other leg is unaffected. Thanks, John
 
My first guess would be a neutral issue, which you basically addressed.

Does switching the unaffected line's load affect this line's voltage?
 
LEDs offer TONS of noise, reactive power, weird harmonics from rectified drivers that do weird things to voltage. Who knows?

I would be really interested to see this with a line reactor installed and see what the readings are. Something really common right now is ECM blower fans in homes causes some flickering. We are recommending line reactors on the indoor HVAC unit. It has already worked in one instance. In the other it did nothing. ???
 
LEDs offer TONS of noise, reactive power, weird harmonics from rectified drivers that do weird things to voltage. Who knows?

I would be really interested to see this with a line reactor installed and see what the readings are. Something really common right now is ECM blower fans in homes causes some flickering. We are recommending line reactors on the indoor HVAC unit. It has already worked in one instance. In the other it did nothing. ???
Different mfgs?
 
Tried switching circuits same thing. Found a burnt battery charger for the drills, so I'm going with Larry neutral issue. will go through it probably mon.
 