Voltage on the ground with open neutral

The electron man

Senior Member
Location
Nyc
Occupation
Electrician
Hey guys having trouble understanding why when you have an open neutral it can create voltage on the grounding system
 

david

Senior Member
Location
Pennsylvania
Hey guys having trouble understanding why when you have an open neutral it can create voltage on the grounding system
It might be easier to understand if you understand the neutral to be a grounded conductor

An open grounded conductor at the structure dosnt open the grounded conductor in all locations.

Your still going to get a voltage reading from the ungrounded conductors to a ground reference point.
 
Last edited:

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Hey guys having trouble understanding why when you have an open neutral it can create voltage on the grounding system
If there's a break in the service neutral, the load's neutral voltage can rise away from zero.

Since the premises grounding system is tied to that neutral, its voltage to earth rises, also.

Only the grounding electrodes are left to attempt to keep that voltage rise to a minimum.
 