Letting you know that I read this reply.
I will process and comment more tomorrow.
My plan now is to have LOP trip nothing, but simply revert to a low level 50/51 unsupervised- over the normal anticipated LTE current. That way a fault of any kind will trip only through over current elements.
The way I see it is this:
VT fails and short circuits. The bus coupler trips in ~12 cycles on its zone deriving voltage from the healthy bus. Remote zone 2 clears all the lines attached to the effected bus in ~25 cycles. Sensing one phase out at the start of the event transformer bay SEL311C goes into LOP- blocking 21P and enabling a low level 50/51. 50/51 will then trip the breaker of the transformer attached to the effected bus while 21P on the other transformer will not "see" the fault passing through.
Now if we have a bus fault without losing a VT, same sequence but instead transformer bay 311C trips in about 25 cycles on a reverse zone looking into the faulted bus. The other transformer's 21P does not pick up as it is set not to "see" (reach) through the transformer.
To me this is a win-win, or as good as its ever going to get. And yes, I have you to thank over not reaching through the transformers- a really bad idea now that I run the scheme through.