Nuber
State Certified Practitioner of Electrical Arts
- Location
- Colorado
- Occupation
- Master Electrician
I am trying to verify my calculations for the following installation because either I am using improper procedures, the nameplate is incorrect, or the installation manual is incorrect.
Assumptions - 2014 NEC, KW is the same as KVA (unity power factor), UL listed Electric Water Heater (tank style with resistive elements), installation instructions and wiring diagram allow for the unit to be field wired single or three phase for any of the following voltages; 208V, 240V, 277V, 480V
Name plate ratings - single phase 18KW, 75 amps, 240 volts; three phase 18KW, 44 amps, 240 volts
My thought process is that the resistance of the heating elements is the only fixed value. When the voltage is changed then current draw and power consumption will as well.
I am looking for a more detailed procedure/answer in order to determine the validity of my own process if anyone can assist.
2 questions for the nameplate ratings above
Assumptions - 2014 NEC, KW is the same as KVA (unity power factor), UL listed Electric Water Heater (tank style with resistive elements), installation instructions and wiring diagram allow for the unit to be field wired single or three phase for any of the following voltages; 208V, 240V, 277V, 480V
Name plate ratings - single phase 18KW, 75 amps, 240 volts; three phase 18KW, 44 amps, 240 volts
My thought process is that the resistance of the heating elements is the only fixed value. When the voltage is changed then current draw and power consumption will as well.
I am looking for a more detailed procedure/answer in order to determine the validity of my own process if anyone can assist.
2 questions for the nameplate ratings above
- What is the NEC branch circuit and OCPD rating for single and three phase if a 208 volt circuit is used?
- What is the real power consumed for single and three phase use by the appliance when the circuit is 208 volts?