We are starting a new house today and this morning I had to install the bonding jumper on our temporary. The neutral bar is insulated from the panel and the ground lug is mounted to the panel. They provide a solid piece of copper wire to bond with.
Before I installed the bonding jumper I checked voltages and out of curiosity I checked voltage from a hot leg to the 4x4 post that the set up is mounted on. It's a treated post and probably holds some moisture and I was reading anywhere from 60-80 volts.
That made me wonder. If the bonding jumper wasn't installed and a fault occurred, obviously there wouldn't be a low impedance path and trip the breaker quickly but lets assume that the 4x4 post provide a path through the ground and back to the source.
What would that do to the voltage on the metal parts affected by the ground fault?
I know If there is no path then metal parts would be at line voltage. What happens when there is a high impedance path back to the source.
This scenario could also happen in a home where the neutral and ground bars are isolated from each other and someone only lands the GEC on the ground bar thinking that will "ground" everything.
Thanks
PS- very busy today.... Will check back in as soon as I can.
Before I installed the bonding jumper I checked voltages and out of curiosity I checked voltage from a hot leg to the 4x4 post that the set up is mounted on. It's a treated post and probably holds some moisture and I was reading anywhere from 60-80 volts.
That made me wonder. If the bonding jumper wasn't installed and a fault occurred, obviously there wouldn't be a low impedance path and trip the breaker quickly but lets assume that the 4x4 post provide a path through the ground and back to the source.
What would that do to the voltage on the metal parts affected by the ground fault?
I know If there is no path then metal parts would be at line voltage. What happens when there is a high impedance path back to the source.
This scenario could also happen in a home where the neutral and ground bars are isolated from each other and someone only lands the GEC on the ground bar thinking that will "ground" everything.
Thanks
PS- very busy today.... Will check back in as soon as I can.