kvramesh said:
I'm concerned about the voltage regulation to the motors...isnt that going to be really bad. the secondary voltage at full load will be much lower than 480V due to this 7.5% impedance.
...
You are focused on just one piece of the system. You haven't given us much information about the rest system. You will need to look at the rest of the xfm data, motor sizes, kva load, feeder sizes, feedr lengths, might even have to call the mfg and get the xfm X/R ratio. You have a whole system to look at.
Your concern is voltage regulation, so sketch out the system, put in the known data, calculate the Vd out to the motors of concern. Could be the feeders cause more Vd that the xfm. To understand, you will need a vector diagram for the xfm and maybe the feeders as well. Chapter 9(?) of the NEC has a pretty good section on the feeder Vd out to normal industrial loads.
Transformer impedance is just one piece. Just because it is 7.5%Z doesn't mean it's bad. I have seen 2%Z and 12%Z. They all have their purpose.
kvramesh said:
...what % of voltage drops are allowed from tranfo ->LV Switchgear ->MCC ->motor according to ANSI? ...
I don't know what ANSI says. You may have to dig out the Specs and read them.
Most 480V motors are rated at 460V. Generally running 5% low (440V)doesn't hurt anything. But that could depend on your loadiing. A motor loaded right up into the service factor could easily run hot if the voltage is low
kvramesh said:
...red book is little confusing to me
Yeah, that is a problem - takes me additional research sometimes. Get some more books, talk to your senior engineers, might consider looking into some seminars. Even after 35 years I try to go to school every year on something.
carl