Greetings all,
I'm wanting to do durability testing on prospective power supply replacements from our current vendor. Because of the number of failures we've seen in the field, names and application details are witheld to protect the guilty
These supplies operate on a single leg of 480 leg-leg of 3 phase delta circuits, or at 277 on a 3phase wye configuration. In situ measurements of on-site power at various industrial client locations have shown V_peak of 1000V+ for durations of 1-5 milliseconds, plus some secondary ringing. The tend to coincide with contactor-based events.
I'm hoping to build/buy a widget to be able to whack potential PSU suitors with transients (either with or without reactors/snubbers) and see how tough they really are. Before I go try to mock something up, I thought I reach out to the community to see what you recommend, as I assume that creating these kinds of spikes in a predictable fashion is a solved problem in certain circles.
I don't need a fancy solution, just something that will help quickly thin the herd as we investigate other vendors.
Thanks as always!
-Phil
P.S. These supplies are implemented in the field with line reactor/snubber pairs, and we've still been through multiple revisions on the existing manufacturers product to knock down failures.
Thanks as always!
-Phil