today i went to my uncles store to fix a display case that was shocking people. i measured volts to the other case right beside it and had 90VAC
he said when people touch both cases at the same time they feel a slight zap
i used the loimpedance function on the 117 and had 0 volts
i opened the junction box and found the wire nut missing off of the hot and the case wasnt grounded at all. the hot was barely touching the cover but there was still enough voltage to be felt.
i repaired everything and all is well
why did i measure 90vac with the high impedance meter and nothing with the loz function? i figured it was because the connection was so light that the meter couldnt pick it up because of the meters load.
am i right with my thinking?