160107-2051 EST
Aleman:
To add detail to your statement.
There are many types of AC volt or ammeters. Some of these are full wave rectified average reading calibrated in RMS values for a sine wave (a Simpson 260, Fluke 27), peak reading calibrated in RMS on a sine wave (I never saw one), peak reading calibrated for the peak value, an electrodynamometer (a true RMS electro-mechanical) (typical old large Weston meters), an electronic true RMS (Fluke 87), a hot-wire true RMS, and iron vane (some are somewhat good at RMS measurement), and electrostatic.
All ordinary meters, mechanical or electronic, do some sort of averaging. An oscilloscope does not average, other than by a bluring, unless some additional processing is done.
The nature of the signal being measured and your measurement goal will determine what is the best type meter to use, and/or how to use or interpret the reading.
Inexpensive UPSs tend to use a pulse type waveform. A scope is a good way to look at the peak value, and a true RMS meter to measure its effective value. Peak is important because that is what is needed by a full-wave rectified capacitor input filter (input to a computer). RMS is need for heating effect.
Wherever you are interested in resistive heating with a complex AC current or voltage waveform use a true RMS meter.