My question is whats the difference between the two. Don't they work relatively the same function. I know that the fire dampers tie in to the fire alarm system with a relay or am i mistaken
eager2learn said:I know that the fire dampers tie in to the fire alarm system with a relay
thanks for this answer it makes things a lot easier to understand knowing that fire dampers are located next to fire rated walls - which would automatically close the damper controlling or limiting the oxygen in those rated walls - correct.infinity said:VAV's are used to control air flow into certain areas and are usually located just about anywhere within the ceiling and controlled by a T-stat or BMS type system. Fire dampers, or fire smoke dampers as they're sometimes called, are located right where the ductwork passes through a fire rated wall and are designed to close under an alarm condition. These are different than VAV's which are designed to control normal airflow of an HVAC system.
eager2learn said:so is it safe to say that when ever there is a fire rate wall there should also be a damper
ItsHot said:they can close with enough force to break your arm!!
You do see a lot of that. Why is it that those blue wire guys get away with anything?keesha said:If you look real close at those dampers.. You will see what a nice easy path it is for the Network guys to route their cables (and others).:roll:
quogueelectric said:One type is electrically activated through a relay in the facp for which there is no fusible link. The other is a fusible link type which is not tied into the facp. Now that I think of it I have seen pneumatic types also which may or may not have status switches tied in to the facp. Almost all of the newer systems I have done are electrically driven motors.
ItsHot said:You do see a lot of that. Why is it that those blue wire guys get away with anything?
keesha said:You do have fire dampers that seperate space for return air plenums (those I referd to).
You have fire dampers for duct returns, smoke evac and others.
Return air plenums most commonly will have the thermals (links).
The others are usualy powerd open and spring closed (open or closed what ever is called for) In any event, What ever position they are to be in during a fire/emergency situation, they will be set to that via springs. Thats' the fastest way to get them in that position. Typicaly.there are of course variables that come into play.