New concrete dock is planned to be installed. The panel has cable entry area on the bottom of 30" x 10". The panel is a floor mount and will fit over an access area (depression/hole in the concrete dock, chases from there to the power centers to install the W cables will be under the concrete).
The problem is the connectors for these cables are so large that we cannot get all the connectors into the 30" x 10" area (for those that want to know, (4) 350kcmil, (6) #3/0, (10) #2, (1) #6, all 4-cond, Blk,Red,White,Green).
One possible solution would be to install a tight fitting chase nipple in the bottom of the enclosure and then wire tie the cable to a support in the bottom of the panel to keep it stationary. I think that would meet the intent of the code for not allowing tension to be passed onto the terminations, but ........ seems shoddy.
If shoddy is the only way we can get this installed, do you believe the NEC would allow it or no?
I'm going to try to sketch this up and visit the AHJ on Friday, but I sure would like to hear y'all opinions before I go. You know I lack self confidence :happysad:
The problem is the connectors for these cables are so large that we cannot get all the connectors into the 30" x 10" area (for those that want to know, (4) 350kcmil, (6) #3/0, (10) #2, (1) #6, all 4-cond, Blk,Red,White,Green).
One possible solution would be to install a tight fitting chase nipple in the bottom of the enclosure and then wire tie the cable to a support in the bottom of the panel to keep it stationary. I think that would meet the intent of the code for not allowing tension to be passed onto the terminations, but ........ seems shoddy.
If shoddy is the only way we can get this installed, do you believe the NEC would allow it or no?
I'm going to try to sketch this up and visit the AHJ on Friday, but I sure would like to hear y'all opinions before I go. You know I lack self confidence :happysad: