WA State Exam
resistance
WA
Need a heads up on rather the WA State Admins exam has questions on taxes?
Also, I head that the major calculations section has a 2 hour limit for four questions??Is this part that hard?? If you have the four post them, or send it to me in private.
Also, I keep hearing that the DLC are confusing. Maybe we should have our test examined (audit the test for review).
Thanks for your help!
davenoiz
Re: WA State Exam
7 questons, 2 hours. i've not passed it yet, and it is hard, for me anyway. i have used all the time. 2 duplex load calc questions, opt and standard. 2 multi-dwelling, opt and standard. one SOB of a comercial two tennent load calc. multi motor load calc and multi motor single and 3 phase VA calc. good luck, bought Mike Holt electrical exam prep book just for the calcs and it has staightened me out on a few things, 80 bucks and worth it.
snapco
Re: WA State Exam
I agree it is a tough 7 questions and it should be at least 21/2 hours. No one will let you know which ones you missed or got right. I have one that I think I missed, if anyone could help with it, I would be grateful-
Calc total VA- 460V 3p service w/ xtfr for 115/230
motors-115v 1ph 5hp nameplate-46.8 amps
230v 1ph 7.5hp nameplate 33.2amp 5min intermit
230v 1ph 10hp nameplate 41.5 amp
460v 3hp 7.5 hp nameplate 9.13
460v 3ph 20 hp nameplate 22.41 5min intermit
460v 3ph 40hp nameplate 43.16
a)104,478 b)113,913 c)96,384 d)93,675