was asked to temp test the Wago 222 connector
i thought in their pdf of the product says max 30A, but the item itself is stamped 20A, so i took it right to 20A with TC taped to its belly. free air test just to see where 20A takes it. ah, their pdf says "Current intensity 32A". not really sure what that means.
![wago222_412.jpg wago222_412.jpg](https://forums.mikeholt.com/data/attachments/6/6408-5bb8fa372754a807addf411a92c12d61.jpg)
was asked to temp test the Wago 222 connector
i thought in their pdf of the product says max 30A, but the item itself is stamped 20A, so i took it right to 20A with TC taped to its belly. free air test just to see where 20A takes it. ah, their pdf says "Current intensity 32A". not really sure what that means.