C codewarrior321 Member Sep 21, 2009 #1 Hi, Question is what Type of occupancy is awaiting for the purpose of general lighting load, as far general lighting load table. Last edited: Sep 21, 2009
Hi, Question is what Type of occupancy is awaiting for the purpose of general lighting load, as far general lighting load table.
raider1 Senior Member Staff member Location Logan, Utah Sep 21, 2009 #2 I would treat it as an office building and apply 3 1/2 volt-amperes per square foot. Chris